[BC] 3 phase to single phase conversion
RichardBJohnson at comcast.net
RichardBJohnson at comcast.net
Mon Feb 9 15:49:05 CST 2009
Your phase converter is either defective or improperly sized if it has the
problems you cite.
Naturally, it is best to have three-phase at the site. However the electric utility
company will often not run three-phase up the side of a mountain to feed your
"inconsequential to them" load, unless you spend about $50,000 per mile
on an existing feed.
I have used properly-sized phase converters on several mountain-top sites
including one with a 125 kVA demand. That was a big one made by Roto-Phase.
They will start fine if they don't have a load on them while starting.
Plus they are extremely quiet unless just left on their shipping pallet which
will act like a sound-board. They need to be properly mounted as specified
by the manufacturer.
The generated phases will have the same regulation as the single-phase
input, It has no choice, the phases will be balanced unless the machine
is improperly sized so it runs at a slip-speed. The single-phase input
will have an ampacity that is 1.73 times the load currents on the output
phases. Therefore. the service entrance needs to be sized correctly.
----- Original Message -----
From: "k7cr" <k7cr at blarg.net>
I have couple comments about these critters.
1- If at all possible, get the power company to install real 3 phase.
2- Consider a transmitter that will operate on Single Phase.
3 -Compare the costs of replacing the transmitter with something with
switchers that will run on single phase to the cost of the phase
converter.
4- NO these things are not silent, at least the type that I am familiar
with (running a 20-25Kw FM Rig) And they generate a good deal of heat.
They need a separate room and ventilation.
5- Beware of inrush on start up....I can be large. Don't even think of
using your Aux Generator to start one. (Unless you have a BIG genny)
6- Note that your regulation will be very poor. For example, I had to
modify the filament regulator in a transmitter to provide for more
range from Filament on only to both filament and plates on.
7- Be very careful about which phase you connect to what in your
transmitter. Before you do this, carefully check with the Tx maker.
(This is all due to the relatively poor regulation of the generate
phase)